Back with another question.
I have a 220V 50A receptacle in my garage. I'm planning on replacing it with a subpanel so I can keep the 50A 220v and also get some 110V 20A and 110V 50A for my friends RV if he comes to visit.
I know that I can't use all the stuff at the same time, just as I can't draw 15A from each receptacle on a lighting circuit.
The CH subpanel they sold me has only one bar for connecting ground and neutral wires. They said to use the same bar for both. [img]/forums/images/icons/ooo.gif[/img] Is that correct procedure? The entrance panels have two bars, one for ground wires and one for neutrals.
This subpanel is being fed with #6 red/black/white, and bare ground.
Just looking for reasurance I guess. [img]/forums/images/icons/laugh.gif[/img]